Water Hammer Pressure Spike Review, Equations and Calculator
Fluid Flow Table of Contents
Water Hammer Pressure Spike Review and Equations
When any moving fluid (not just water) is abruptly stopped, as when a valve closes suddenly, large pressures can develop. Although detailed analysis requires knowledge of the elastic properties of the pipe and the flow-time history, the limiting case of rigid pipe and instantaneous closure is simple to calculate.
A pressure spike is the resulting rapid rise in pressure above static pressure caused by water hammer. The highest pressure spike attained will be at the instant the flow changed and is governed by the following equation.
Δph = ρ · cs · V / gc
Δph = pressure rise caused by water hammer, lbf /ft2
ρ = fluid density, lbm/ft3
cs = velocity of sound in fluid, fps
V = fluid flow velocity, fps
gc = gravity ft/sec2
The cs for water is 4720 fps, although the pipe’s elasticity reduces the effective value.
Example water hammer calculation:
What is the maximum pressure rise if water flowing at 10 fps is stopped instantaneously?
Solution:
Δph = 62.4 lbf/ft3 x 4720 fps x 10 fps / 32.2 ft/sec2 = 91,468 lb/ft2 = 635 psi
Conversion:
1 lb/ft2 = 0.0069444444 psi
1 psi = 144 lb/ft2
- Pressure Vessel Design Formula and Calculators Resources
- Water Hammer Accumulator Sizing Excel Spreadsheet Calculator
- Steam Hammer Review
- Water Hammer (Waterhammer) Review and Equation
- Operational Considerations Practical Applications Water Hammer
- Impact Loading Approximate Formulas
- Mass Impact Loading Equations
References
- ASHRAE Handbook of Fundamentals, 2021 Inch-Pound Edition